You want to hear crazy? I was speaking to an electrician in an older section of PA who said they used to use the ground as a neutral. No, that is not bonding the neutral and ground at the box, but actually using the ground as the second current carrying wire. That is as bad as the common practice among boneheads that have a backup generator and feed it into a dryer outlet, using the ground at the three wire socket as the neutral for the 120 volt circuits. And to add salt to the wounds they have no transfer switch and try to remember to trip off the main service disconnect.


Top
 Profile  
 
 Post subject: Re: Better earth grounds
PostPosted: April 30th, 2020, 9:13 am 
Offline
User avatar

Joined: July 24th, 2015, 4:17 pm
Posts: 1880
Location: Parkville, Maryland
Stuart Polansky wrote:
8 foot ground rods should be considered supplemental only. Their impedance is ridiculously high; no matter how large the service (even 4000 amperes) the grounding electrode conductor to a driven rod never needs to exceed #6 AWG copper!!!!! The rod simply cannot conduct any more current.

Want a good ground besides the superb cold water ground? Use a Ufer ground. That is a foundation ground. If there isn't one in your house, the procedure is to dig a 20 foot long, two foot wide by two foot deep hole, install rebar, Cad weld the GEC to the rebar, and encase the assembly in concrete. That is a low impedance ground.

If you are going to drive a shitty ground rod and connect it to your stereo, consider this . Unless, you have a separately derived system (transformer coupled, galvanic isolation, no current path between primary and secondary windings) the ground you add is in parallel with the household grounding electrode system as well as the utility center tap of the transformer feeding the service.
So, if a ground fault occurs anywhere between the transformer and any branch circuit in the house, a portion of the fault current WILL flow through your stereo ground, perhaps right through your tonearm!

There are good reasons for the Code rules. Flout them at your own risk.

ALL GROUNDS IN A STRUCTURE NEED TO CONNECT TO THE GROUNDED CONDUCTOR (NEUTRAL) AT A SINGLE POINT UNLESS WORKING WITH A SEPARATELY DERIVED SYSTEM!


A good argument for following the National Electrical Code (NEC). These issues were and are not arbitrary. The code was developed over many decades and revisions to the code are based on new problems not addressed previously.

The "problems" were and are real failure/fault events. Safety is first and foremost the driving criteria including fire protection requirements.

_________________
Walt


Top
 Profile  
 
 Post subject: Re: Better earth grounds
PostPosted: April 30th, 2020, 9:27 am 
Offline
User avatar

Joined: July 24th, 2015, 4:17 pm
Posts: 1880
Location: Parkville, Maryland
tomp wrote:
You want to hear crazy? I was speaking to an electrician in an older section of PA who said they used to use the ground as a neutral. No, that is not bonding the neutral and ground at the box, but actually using the ground as the second current carrying wire. That is as bad as the common practice among boneheads that have a backup generator and feed it into a dryer outlet, using the ground at the three wire socket as the neutral for the 120 volt circuits. And to add salt to the wounds they have no transfer switch and try to remember to trip off the main service disconnect.


You should see some of the crazy things I observed over the past 25 years performing due diligence and condition assessment studies of Class-A office buildings and residential towers. "Stupid bonehead stunts" are not limited to the residential home.

My favorite pet-peeve is not performing recommended preventive maintenance only to find out that a client had to spend $250K to replace a switchboard that not only failed but created a fire event. PM applies to the home as well. Those screw fittings in a panel-board will slowly loosen over time due to thermal cycling. When loosened enough you have a relatively high contact resistance with the resultant voltage drop and heat. And now -- the new love child of the NEC are flash-over faults that standard thermal circuit-breakers "do not see."

_________________
Walt


Top
 Profile  
 
 Post subject: Re: Better earth grounds
PostPosted: April 30th, 2020, 11:58 am 
Offline
User avatar

Joined: February 28th, 2013, 3:31 pm
Posts: 1872
Here is the spec for "breakers" in my new house under construction. As you mentioned they are arc fault interrupters that look for high frequencies on the line caused by arcing.


Attachments:
Arc fault interrupter.png
Arc fault interrupter.png [ 15.76 KiB | Viewed 15464 times ]
Top
 Profile  
 
 Post subject: Re: Better earth grounds
PostPosted: April 30th, 2020, 1:10 pm 
Offline
User avatar

Joined: July 24th, 2015, 4:17 pm
Posts: 1880
Location: Parkville, Maryland
tomp wrote:
Here is the spec for "breakers" in my new house under construction. As you mentioned they are arc fault interrupters that look for high frequencies on the line caused by arcing.


Yes. That's the current code requirement and has been in effect since 2015.

_________________
Walt


Top
 Profile  
 
 Post subject: Re: Better earth grounds
PostPosted: April 30th, 2020, 1:23 pm 
Offline
User avatar

Joined: February 28th, 2013, 3:31 pm
Posts: 1872
I spoke to a couple of electricians who said certain appliances like vacuum cleaners drive the arc fault suppressors crazy. One of the electricians said when working on new construction where contractors are using saws with electric brakes, he installs regular breakers while they are working or the interrupters would trip repeatedly when they stop the saws. When they are finished he goes back and replaces the standard breakers with interrupters. They are another case of good ideas with unforeseen consequences.


Top
 Profile  
 
 Post subject: Re: Better earth grounds
PostPosted: April 30th, 2020, 2:05 pm 
Offline
User avatar

Joined: July 24th, 2015, 4:17 pm
Posts: 1880
Location: Parkville, Maryland
tomp wrote:
I spoke to a couple of electricians who said certain appliances like vacuum cleaners drive the arc fault suppressors crazy. One of the electricians said when working on new construction where contractors are using saws with electric brakes, he installs regular breakers while they are working or the interrupters would trip repeatedly when they stop the saws. When they are finished he goes back and replaces the standard breakers with interrupters. They are another case of good ideas with unforeseen consequences.


I get that. The motor commutators!! Who knew?

_________________
Walt


Top
 Profile  
 
 Post subject: Re: Better earth grounds
PostPosted: April 30th, 2020, 4:12 pm 
Offline

Joined: February 28th, 2013, 3:31 pm
Posts: 373
tomp wrote:
I spoke to a couple of electricians who said certain appliances like vacuum cleaners drive the arc fault suppressors crazy....

I just experienced this with our recent remodel. Had to clean the vac motor and install new brushes, which improved it 90%, but there's still a circuit we have to avoid using. It's definitely the vacuum too. I can plug in my shop vac or any other tool into that circuit without a problem. Plug in the house vacuum and it trips.

As Tom said, a real good idea that just came up a little short.


Top
 Profile  
 
 Post subject: Re: Better earth grounds
PostPosted: April 30th, 2020, 5:23 pm 
Offline
User avatar

Joined: December 14th, 2013, 2:19 pm
Posts: 1033
tomp wrote:
You want to hear crazy? I was speaking to an electrician in an older section of PA who said they used to use the ground as a neutral. No, that is not bonding the neutral and ground at the box, but actually using the ground as the second current carrying wire. That is as bad as the common practice among boneheads that have a backup generator and feed it into a dryer outlet, using the ground at the three wire socket as the neutral for the 120 volt circuits. And to add salt to the wounds they have no transfer switch and try to remember to trip off the main service disconnect.


Tom, I feel your mental anguish!

There is no licensing for electricians or electrical contractors in PA. I figured there was reciprocity with MD, so contacted PA about getting my masters there. Nope, nothing! Good luck, since my casual observations of new builds in my area of PA show real deficiencies, not just nit-picking.

Yeah, we detest arc-fault breakers, both series and shunt type cause unwanted nuisance tripping and play havoc with some older installations. Some AHJ are demanding AFCI be installed on all circuits when a heavy-up is performed. That's not a NEC requirement, but it is their prerogative.

Using a grounding/bonding conductor or means (enclosures and raceways) is colloquially called "bootleg neutral". Really stupid and dangerous practice. There is obviously a voltage "drop" across a current-carrying conductor, such as a "grounded wire" AKA Neutral. Grounding means (the green wire) are by definition to be AT ground potential. The use of the "ground" as a neutral raises its potential to above ground, sometimes substantially so! So, if Harry or Harriet Homeowner gets between a real grounded terminal like a faucet and a clothes dryer which has an enclosure at a few volts above ground, we get to read about it in the paper, on occasion.

In the special case of 120/240 volt clothes dryers, that actually used to be allowed until 1990 or so (I forget). Many older dryers have a 3-wire connection, where neutral and ground are a shared connection. This was ONLY ever allowed in the special case of single family homes and connected to the main electric panel (where neutral and ground are connected), not a subpanel (where neutral and grounds are separated). I guess the judgement was that the only neutral loads in the dryer are controls and the tumbler motor. Yup, we see these ALL the time in apartment buildings, commercial spaces and just about everywhere else. We get the call, customer has a new dryer and cord, needs a receptacle. We will not hook it up without providing a 4-wire cord. It's Code and it's ignored.

Thank goodness that G-d looks out for us; we seem to have zero respect for something in our homes that can kill us.


Top
 Profile  
 
 Post subject: Re: Better earth grounds
PostPosted: April 30th, 2020, 5:47 pm 
Offline
User avatar

Joined: February 28th, 2013, 3:31 pm
Posts: 1872
Most of the three conductor 240 outlets I have seen on dryers, ranges, etc are L1, L2, and ground with no neutral as they don't need 120 volts. On the other hand you can get regulatory agencies that go overboard. We had a graphic arts pulsed xenon lighting system that operated on 240 volts and inside was an autoformer with taps to select the appropriate setting for either 208 or 240. It also had a 120 volt tap to run fans in the lights. It had a 3 wire connection as there was no need for a neutral seeing that everything came off the autoformer. It got UL approval but when we submitted it to the City of LA for their approval they rejected it because there was no neutral and the fans were 120 volts. We tried to explain to them that the 120 volts was not derived from a neutral connection but rather the autoformer. They still would not listen. So, we installed a 4 wire cord and plug but only used 3 wires inside. They approved it. :crazy:


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 41 posts ]  Go to page Previous  1, 2, 3, 4, 5  Next

All times are UTC - 5 hours [ DST ]


Who is online

Users browsing this forum: No registered users and 35 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Powered by phpBB® Forum Software © phpBB Group