 Post subject: AC power quality story
PostPosted: January 22nd, 2018, 3:13 pm 
Offline
User avatar

Joined: January 13th, 2016, 9:14 pm
Posts: 787
A long time ago I noticed that the toroidal power transformers in my amps were humming pretty loudly. At the time was experimenting with balanced power and other AC cleaning stuff, so bought a Fluke 43B power line analyzer.

The distortion measurement capability gave interesting results. Checked a friends house and the distortion was 2% THD. Came back to my place and it was 6% THD. We had a lightning strike in the neighborhood a few years prior and that was the only clue.

Called the local electric company with the data and they sent out a crew to check. Verified my data and then looked at the meter base. They pulled it and the contacts were corroded and black. They cleaned them with a cloth and reinstalled the meter. Measure it again and the distortion was down to 2% THD. Checked the toroids and they were quiet again.

Since DC is created when distortions is present (probably due to contact rectification from the corrosion and carboning), that was the cause of the toroid hum. Down to normal levels for years. Recently the meter was changed to the new digital style, so will have to make measurements again to see if there is any change.

Fun with AC power and a good analyzer.


Top
 Profile  
 
PostPosted: January 22nd, 2018, 4:03 pm 
Offline
User avatar

Joined: January 15th, 2015, 7:19 am
Posts: 1697
Location: Baltimore MD
This is interesting. I have two 200 watt SS amps with toroid xformers and the buzz for about a few seconds on turn on,
then quite down but every once in a while the buzz stays on until I turn them off.
I have read that there are circuits to remove DC from the AC line but never built any.
The builder of the amps says the few seconds of buzz at turn on is normal.


Top
 Profile  
 
PostPosted: January 22nd, 2018, 4:05 pm 
Offline
User avatar

Joined: February 28th, 2013, 3:31 pm
Posts: 1780
I had weird waveforms on my AC line one time and the power company did not believe anything was wrong until I sent scope traces to one of their engineers. They found out it was a power factor correction device on a local pole and one of the capacitors was bad. The fixed it and all was better.


Top
 Profile  
 
PostPosted: January 22nd, 2018, 4:06 pm 
Offline
Site Admin
User avatar

Joined: February 28th, 2013, 10:38 am
Posts: 1682
The buzz at turn-on is probably due to the brief period after turn-on where the transformers are actually in an overload situation while charging up the caps...

Roscoe

_________________
I can explain it to you, but I can’t understand it for you.


Top
 Profile  
 
PostPosted: January 22nd, 2018, 4:12 pm 
Offline
User avatar

Joined: January 15th, 2015, 7:19 am
Posts: 1697
Location: Baltimore MD
400AV tranny into 120,000uf lytics


Top
 Profile  
 
PostPosted: January 22nd, 2018, 4:16 pm 
Offline
User avatar

Joined: January 13th, 2016, 9:14 pm
Posts: 787
Yes, a big transformer into big caps buzzes until the caps are charged. If they continue afterwards, then maybe DC on the line. Lots of reasons just like Tom said with his problem.

There are plenty of DC removal circuits out there. Best to get rid of it at the source than try and correct it.


Top
 Profile  
 
PostPosted: January 22nd, 2018, 8:44 pm 
Offline
User avatar

Joined: July 24th, 2015, 4:17 pm
Posts: 1701
Location: Parkville, Maryland
tomp wrote:
I had weird waveforms on my AC line one time and the power company did not believe anything was wrong until I sent scope traces to one of their engineers. They found out it was a power factor correction device on a local pole and one of the capacitors was bad. The fixed it and all was better.



Whoa! Your provider is using power factor correction? Aren't they sticking their hands in their own pockets?

_________________
Walt


Top
 Profile  
 
PostPosted: January 22nd, 2018, 9:39 pm 
Offline
User avatar

Joined: February 28th, 2013, 3:31 pm
Posts: 1780
Pepco is like a lot of other utilities. Having loads on the grid that shift the power factor away from unity causes them a lot of problems so they install banks of switched capacitors to adjust the power factor. I don't know all the details but if you look at the poles in your area you might find a box connected to the high voltage lines. They must have some circuit to detect power factor and add or remove capacitors. These were probably used to balance inductive loads like motors and transformers that have leakage inductance but I wonder how the plethora of switch mode supplies affects their assumptions.


Top
 Profile  
 
PostPosted: January 22nd, 2018, 9:41 pm 
Offline
Site Admin
User avatar

Joined: February 28th, 2013, 10:38 am
Posts: 1682
tomp wrote:
but I wonder how the plethora of switch mode supplies affects their assumptions.


Or their measurements...

Roscoe

_________________
I can explain it to you, but I can’t understand it for you.


Top
 Profile  
 
PostPosted: January 22nd, 2018, 10:00 pm 
Offline

Joined: January 14th, 2015, 11:15 pm
Posts: 499
To change the subject slightly. In many parts of the world, installation of solar panels and batteries is increasing rapidly. Most systems are still connected to the grid but some are off-grid.

If you were to install either system, what would you do to maximize the quality of electricity used by your amplifier?

ray


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 39 posts ]  Go to page 1, 2, 3, 4  Next

All times are UTC - 5 hours [ DST ]


Who is online

Users browsing this forum: No registered users and 48 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
cron
Powered by phpBB® Forum Software © phpBB Group